Every contractor is different. I get that.

We don't all need to do everything the same way or include the same services with repairs, but there are some “best practices” that can save you a lot of heartache before, during, and after you make a big repair.

Catch it During Diagnosis

Let's say you find a failed, shorted compressor on a 7-year-old system that still has manufacturer parts coverage. If you simply quote the compressor and leave, you may be missing many other maintenance-related issues that can affect operation once the compressor is replaced. A shortlist of items to check would be:

And this is just for cooling side issues. If the system is a fuel-burning appliance, you will inspect every part of the furnace operation.

  • Venting
  • Condensate drainage
  • Burners
  • Flame proving
  • Safeties

And much more…

Testing all of these things is commonplace AFTER a repair. Still, it makes so much more sense to do it beforehand so that you can either charge appropriately for any of these items that need to be addressed or let the customer know you are including those items to differentiate you from the competition.

Things to Do Along With Major Repairs 

There are a few things you need to do during major air conditioning or refrigeration repairs because they just make good sense to prevent callbacks. You can include them in the price or not, but either way, it will save you more than it costs to do it.

  • Visually inspect the entire system for wiring damage, poor connections, excessive corrosion and refrigerant oil
  • Clean the drain line and condensate pan. (Seriously, do this. Here's a guide.)
  • Wash the condenser coil
  • Clean the blower wheel if it is dirty. (Even if you've heard otherwise, you should still clean it if it's dirty.)
  • Change the air filter
  • Test all modes of operation
  • Ensure system airflow is correct (at minimum look at blower settings and static pressure)
  • Measure compressor and evaporator superheat
  • Measure subcooling and ensure a proper refigerant charge

Do these things along with all the standard tests you perform to ensure that you have no issues and that whatever caused the fault in the system has been rectified. Being thorough will save you a lot of problems. When the customer spends a lot of money getting a system fixed, they don't want to turn around and have it fail for an “unrelated” reason.

While this list is clearly tailored to the residential and light commercial air conditioning market, every piece of equipment has its common maintenance items. So, what do you do whenever you make a major repair?

—Bryan

 

Comments

Carl Slevin
Carl Slevin
1/17/18 at 10:08 PM

Good list but should be done on every call not just major repairs.
Gas furnace
•Check/clean drain lines & trap
•Inspect intake/exhaust for proper slope & termination, blockage
•Clean flame sensor
•Ohm out ignitor
•Check/clean blower, filter, evap coil, & if suspected to possibly be dirty secondary heat exchanger
•Temperature rise & if needed manifold pressure & duct static pressure
•Inspect heat exchanger
•Teat high limit

Dave Miller
Dave Miller
1/18/18 at 06:13 AM

Great point. In your example if we do a compressor, we have codes in our system that tells to replace the : Dryer, contactor and capacitor. even if they are in good shape. A compressor is too expensive to have it fasil in a week or a month. $40 in extra parts ensures you will have a compressor that stays working.

Bill Allen
Bill Allen
11/12/21 at 09:56 PM

Treat your service calls like tune ups and treat your tune ups like service calls

Alice Carroll
Alice Carroll
3/17/22 at 08:41 AM

Thanks for the reminder that overheating is actually one of the common problems that air conditioners have at some point. I plan to get air conditioning repairs for that soon. It seems that mine has been guzzling a lot more electricity nowadays.

https://www.winstonsheetmetalandhvac.com/

Related Tech Tips

Don't Forget the Panel
See the photo above? This is a unit we (my company) serviced for a commercial customer. It doesn't matter if we aligned the belt, dialed in the charge, cleaned the condenser (using THIS thorough process), and got the drain pan clean. We look like dummies because the panel fell off. Also, as you may notice, […]
Read more
Our Best 3D Animated Videos
Over the past year, we have been adding 3D animations to our YouTube channel. It can be difficult to film everything we do in the field, so we've found 3D animations to be a helpful tool to show how parts work and how to do certain tasks. So far, we've uploaded nine 3D animations. This […]
Read more
Condensate Pump Drains
One of my techs (Jim Walch) brought another common “double trap”-style issue to my attention: techs and installers running a drain too far into a condensate pump. When you run the system drain too deep into the pump reservoir, the water level can rise high enough to cover the drain end. That can create the […]
Read more
loading

To continue you need to agree to our terms.

The HVAC School site, podcast and daily tech tips
Made possible by Generous support from